No.
First of all, that's a really small beam (8" wide x 12" deep). Trying to fit shear reinforcing in such a narrow beam will be nearly impossible. ACI 318 requires 1.5" of cover on all sides to the shear reinforcing.
But to answer your question, the maximum permitted spacing of the shear reinforcing is d/2, which for this beam is about 5". The only way you can avoid that maximum permitted shear reinforcing spacing requirement is if the required shear strength Vu is less than 0.5 x phi Vc, in which case you don't need any shear reinforcing.