can I use Different voltages in same duct bank

Status
Not open for further replies.

Samamelectric

Electrical
Aug 19, 2009
2
Can I run a 12,470 volt conduit in the same duct bank as my 480 conduits? If not how much separation would I need?? I have look in the NEC but can't seem to find anything on this. Any input would be appreciated.

 
Replies continue below

Recommended for you

See section 300.3(C)(2): Not allowed except permitted in a) through (e).

I have 2005 NEC with me.

______________________________________________________________________________
This is normally the space where people post something insightful.
 
That NEC article refers to running different voltage systems within the same conduit or cable. It does not apply to running different voltage system in different conduits within the same duct bank. This is allowed. It is permissible to run a 12 kV circuit in one conduit, a 480 V circuit in another conduit and a 24 V dc circuit in a third conduit within a common duct bank. The problem come when you enter a manhole or handhole, since the high voltage must be isolated from the lower voltages.

We generally split out separate manholes/handholes for the 15 kV (or any medium-voltage) cables. Then if you use 600 V insulation for all low-voltage cables, they can occupy the same space in a manhole/handhole. The other option is to provide a barrier of some type within the manhole to isolate the 12 kV from the lower voltages.

It's good practice to keep the 12 kV ducts segregated in one portion of the duct bank. We sometimes put two duct banks in a common trench to increase separation, but this is not required by the NEC, AFAIK.
 
Yes...I need to read the OP better...



______________________________________________________________________________
This is normally the space where people post something insightful.
 
Thanks. Thats what I thought. I looked in the code book and could not find anything. Thanks again for all the reply's.
 