Can you use a three-phase circuit breaker for a single phase load?

Status
Not open for further replies.

bdn2004

Electrical
Jan 27, 2007
792
0
0
US
I've got to hook up a small single phase control power transformer. I have a spare 480V 3-phase breaker in the control panel already wired in. I like it because it's a relatively expensive breaker that is monitored by a PLC. Is it legal to wire this this way?
 
Replies continue below

Recommended for you

Depending on the size of the breaker, you may have to add overload and over-current protection for the transformer and the transformer primary conductors.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 