Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cantilever Retaining Wall Frost Depth

Status
Not open for further replies.

Ceinostuv

Structural
Aug 16, 2018
52
A colleague of mine is studying for the PE exam and came across a note that reads "To prevent frost heaving, the top of the base should be below the frost line. This establishes a minimum wall height, H." in reference to cantilevered retaining wall footings. Does anyone practice this and/or have an explanation for why they would be different from other walls? We can't seem to find a source for this and have typically specified bottom of footing at frost depth (also typically dictated in the Geotech reports we receive for these projects).

Judgement-In-Training
 
Replies continue below

Recommended for you

Sounds like a mistake in the verbiage.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
The NYSDOT standard is to place the bottom of the footing at the frost depth.
 
Frost penetrates deeper when the wall is not adjacent to a heated space, so frost depth outside the wall of a heated building will be shallower than a retaining wall in an open field. Another factor would be depth of snow, so if the retaining wall is adjacent to a road or sidewalk which will be cleared of snow in winter months, the depth of frost will be substantially greater.

It is not always practical to place the bottom of footing at frost depth. In some climates, that could be eight feet or more. Sometimes insulation is used above and beyond the footing to limit frost penetration.

BA
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor