nightfox1925
Electrical
- Apr 3, 2006
- 567
Hello Friends,
We have just recently reviewed 230kV SF6 power circuit breakers specification and observed that the rated Interrupting Rating of the vendor proposed power circuit breakers are less than the required S.C. value specified by BUYER. The Vendor informed us that adding some specific capacitance at suitable locations would increase the Interrupting Rating of the Power Circuit Breakers. I'm a little bit confused. Is this related to the TRV? can anyone provide me with more clear details on this subject?
We have just recently reviewed 230kV SF6 power circuit breakers specification and observed that the rated Interrupting Rating of the vendor proposed power circuit breakers are less than the required S.C. value specified by BUYER. The Vendor informed us that adding some specific capacitance at suitable locations would increase the Interrupting Rating of the Power Circuit Breakers. I'm a little bit confused. Is this related to the TRV? can anyone provide me with more clear details on this subject?