Capacitor Inrush Current

Status
Not open for further replies.

electricnewbie

Electrical
Aug 6, 2010
12
0
0
US
Hello all,
I’m trying to find the inrush current a new 12 (24MVAR future) 115kv Capacitor bank. I found the formula:

I(max)=1330*?(KVAR/LS) for 60hz,
Where, LS is the system inductance in microhenries.

Now, I know that:
Xl=2?fL=377*L
Or...
L=Xl/(2*pi*f)

So my question is, should I just use the positive sequence X (in ohms given from CAPE) to get my LS? Or should I include the neg and zero sequence X values?


X (ohms)
+seq: 21.505
-seq: 21.525
0seq: 26.356

Thank you in advance.
 
Replies continue below

Recommended for you

That is the typical size of bank at that voltage. Most new bank locations have two 12 MVAR banks, each with their own breaker.

The utility also has several smaller sub-transmission cap banks to support the 115kV voltage.
 