Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SDETERS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Capacity rating Factor Kt in Battery sizing - IEEE 485

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
441
As in IEEE-485,

Kt_factor_IEEE_485_r96eli.png



Kt factor is the ratio of rated Ampere-hour capacity to the Amperes that can be supplied by that cell for T minutes at 25 degree celcius to a given end of discharge voltage.

How do we come to know this rated Ampere-hour capacity of the battery before calculating? (as we are doing this to arrive at the same).
 
Replies continue below

Recommended for you

That is usually what the battery is bought as. 100AH, 500AH, 420AH, etc.

Alternatively you can measure it. Measure it at the expected draw for your application.

Keith Cress
kcress -
 
Note that IEEE-485 specifically covers short duration, high-current, draws

But, the question you're asking seems backwards. You determine what capacity you need from whatever is using the battery, i.e., if it's 12V at 1A, or 10A, and you account for the intensity of the draw on the capacity of the battery, and then you select a battery that meets the requirement.

TTFN (ta ta for now)