Dear Discussion Forum (first posting, sorry it's so long),
Greatings from Richmond, Virginia USA. My company's practice is to use a dense-graded aggregate (i.e., minus 3/4-in with about 5 percent passing the 200 sieve - D10 of about 0.15 mm) for the "capillary break" beneath industrial floor slabs. Many in the industry (years ago) used to use an open-graded aggregate for the same purpose (i.e., minus 1-1/2 in with less than 3 percent passing the No. 8 sieve). From my understanding (I'm a geotechnical engineer not a structural engineer) they both serve the same structural purpose (i.e., enhancing the subgrade modulus and also providing a more uniform subgrade condition) and are also intended to serve as a "capillary break" between the subgrade moisture and the underside of the concrete floor slab.
Here's why I write: Looking at Terzaghi's book, the standard equation for capillary rise is Hc=c/(e*D10) using consistent units, where C is in the range of 0.1 to 0.5 cm. When I use this equation for the dense-graded aggregate, the calculated range for capillary rise is somewhere in the range of 23 to 115 cm (9 to 45 inches). As you can imagine this does not seem to offer a very effective "capillary break" when a typical layer thickness is 6 inches.
Being a born skeptic (and hopefully a passible engineer), I decided to do my own "bench test". Here's what I did. I make a column of the aggregate materials in a cylinder and acheived a compacted density of about 120 pcf. Not having a "Proctor" yet (I'm still forumulating my strategy), I figured that this was about 95 percent relative compaction). I submerged the lower inch of the 15-in tall cylinder and waited for capillary movement. Went home for the weekend and when I returned, the water had fully reached the top of the cylinder.
Looking at the post-test moisture contents, I noted that the moisture content in the submerged interval was about 12.2 percent and with increasing height I recorded moisture contents of 11.4 to 9.95 percent. Using the 12.2 as "fully saturated", I concluded that the capillary rise provided from 93.3 to 81.4 percent saturation (again with height).
Here's why I write. While it is undesirable to have fully saturated conditions on the underside of a slab, is there any guidelines to acknowledge whether it's o.k. to have 70 percent saturatation? What about 82 percent saturation?
I typically expect the optimum moisture content for compaction is in the range of 85 to 90 percent, so the typical post-compaction moisture contents would be in this range anyhow.
Does anybody on this forum understand my ramblings? Any comments? Feel free to post or otherwise provide insight.
Sincerely,
Carl "fatt-dad" Benson
Geologist and Engineer
Greatings from Richmond, Virginia USA. My company's practice is to use a dense-graded aggregate (i.e., minus 3/4-in with about 5 percent passing the 200 sieve - D10 of about 0.15 mm) for the "capillary break" beneath industrial floor slabs. Many in the industry (years ago) used to use an open-graded aggregate for the same purpose (i.e., minus 1-1/2 in with less than 3 percent passing the No. 8 sieve). From my understanding (I'm a geotechnical engineer not a structural engineer) they both serve the same structural purpose (i.e., enhancing the subgrade modulus and also providing a more uniform subgrade condition) and are also intended to serve as a "capillary break" between the subgrade moisture and the underside of the concrete floor slab.
Here's why I write: Looking at Terzaghi's book, the standard equation for capillary rise is Hc=c/(e*D10) using consistent units, where C is in the range of 0.1 to 0.5 cm. When I use this equation for the dense-graded aggregate, the calculated range for capillary rise is somewhere in the range of 23 to 115 cm (9 to 45 inches). As you can imagine this does not seem to offer a very effective "capillary break" when a typical layer thickness is 6 inches.
Being a born skeptic (and hopefully a passible engineer), I decided to do my own "bench test". Here's what I did. I make a column of the aggregate materials in a cylinder and acheived a compacted density of about 120 pcf. Not having a "Proctor" yet (I'm still forumulating my strategy), I figured that this was about 95 percent relative compaction). I submerged the lower inch of the 15-in tall cylinder and waited for capillary movement. Went home for the weekend and when I returned, the water had fully reached the top of the cylinder.
Looking at the post-test moisture contents, I noted that the moisture content in the submerged interval was about 12.2 percent and with increasing height I recorded moisture contents of 11.4 to 9.95 percent. Using the 12.2 as "fully saturated", I concluded that the capillary rise provided from 93.3 to 81.4 percent saturation (again with height).
Here's why I write. While it is undesirable to have fully saturated conditions on the underside of a slab, is there any guidelines to acknowledge whether it's o.k. to have 70 percent saturatation? What about 82 percent saturation?
I typically expect the optimum moisture content for compaction is in the range of 85 to 90 percent, so the typical post-compaction moisture contents would be in this range anyhow.
Does anybody on this forum understand my ramblings? Any comments? Feel free to post or otherwise provide insight.
Sincerely,
Carl "fatt-dad" Benson
Geologist and Engineer