I walked into a situation where I'm asked to install a condensate drain with neutralizer on a vent system. Upon investigating, I found that the installation was terrible. There are two (2) 80% upflow furnaces with draft fans in a mechanical room. Input on each is 88,000 BTUH. The vent connectors are 4" single-wall and rise up about 3'. From there they wye into a horizontal 6" B-vent. The 6" B-vent then runs 80' (yes, eighty feet) horizontally. It then elbows up through the roof with only a 5' stack. So total rise height including the connector rise is about 8'.
Shocker! They are condensing in the 80' horizontal run, and they think a drain will somehow help. I'm going to point out the problems and would like a double-check please.
According to the 2018 NFPA 54 table 13.2b, with a 3' riser and an 8' height, the single-wall connector risers should be 5". 4" is not even listed as a possibility for these conditions.
looks like the common header size of 6" B-vent would be correct, provided there were not too many elbows, etc.
Section 13.2.4 states that the length of a common vent manifold shall not exceed 18" per inch of manifold diameter. So, if I am understanding correctly, with a 6" diameter, the horizontal limit is 108" or 9'.
Does this sound right?
Shocker! They are condensing in the 80' horizontal run, and they think a drain will somehow help. I'm going to point out the problems and would like a double-check please.
According to the 2018 NFPA 54 table 13.2b, with a 3' riser and an 8' height, the single-wall connector risers should be 5". 4" is not even listed as a possibility for these conditions.
looks like the common header size of 6" B-vent would be correct, provided there were not too many elbows, etc.
Section 13.2.4 states that the length of a common vent manifold shall not exceed 18" per inch of manifold diameter. So, if I am understanding correctly, with a 6" diameter, the horizontal limit is 108" or 9'.
Does this sound right?