ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
One of distribution utility have a 115-69 kV three phase, wye (grounded) primary and wye (grounded) secondary step-down transformer with one 69 kV feeder line dedicated feeder connected to a nearby 69-13.8 kV delta primary-solid grounded secondary substation with further 13.8 kV feeder lines. This 69-13.8 kV transformer is protected with primary fuses and secondary power circuit breaker with 51/51G relays.
A ground fault occurred at 13.8 kV feeder line and the upstream 69 kV circuit breaker protection relay tripped on 2 phase and ground fault. I am wondering why the upstream relay ground fault protection may have picked up when the downstream transformer primary winding is DELTA.
Is there a way primary fuse will blow at the same time when line-to-ground fault occurs at the downstream transformer secondary?
Thank you for your comments and opinions as always.
One of distribution utility have a 115-69 kV three phase, wye (grounded) primary and wye (grounded) secondary step-down transformer with one 69 kV feeder line dedicated feeder connected to a nearby 69-13.8 kV delta primary-solid grounded secondary substation with further 13.8 kV feeder lines. This 69-13.8 kV transformer is protected with primary fuses and secondary power circuit breaker with 51/51G relays.
A ground fault occurred at 13.8 kV feeder line and the upstream 69 kV circuit breaker protection relay tripped on 2 phase and ground fault. I am wondering why the upstream relay ground fault protection may have picked up when the downstream transformer primary winding is DELTA.
Is there a way primary fuse will blow at the same time when line-to-ground fault occurs at the downstream transformer secondary?
Thank you for your comments and opinions as always.