electricpete
Electrical
- May 4, 2001
- 16,774
OK, here is the situation.
2-pole motor ~ 50hp fed from ungrounded 480 vac system.
Motor tripped on instantaneous overcurrent a few months ago.
As part of investigation - Meggered/bridged motor (sat). Did a start while monitoring current on O-scope (sat). Checked molded case breaker instantaneous trip (sat - within expected bounds based on nameplate LRC and up to factor of 2 increase in 1st peak due to dc component). Breaker was replaced at that time.
Motor has not shown any unusual vibration or other characteristics.
Now this weekend - Motor tripped again on start (instantaneous). Motor meggers and bridges sat again. Voltage is normal.
They called me up at home and want to know: "Is there anything about the motor that can make it susceptible to causing a trip?"
My response is: No. The highest instantaneous peak varies in a random manner based on phase at closing (as we all know). None of the previous tests have shown anything abnormal. I have never heard of a 460vac motor fault that would lead to an instantaneous trip, and then motor subsequently operates fine. I think you need to check your setpoints and make sure they are high enough.
Their response is: the setpoints have been fully checked and are well above that theoretical worst case. We are on the verge of changing out the motor instead of re-revaluating the setpoint. We want to know what is it about the motor that can cause variation in starting current beyond what is predicted by analysis using 2* factor and nameplate data.
Can you help with this question? Any credible faults on the motor that cause an assumed (by others) abnormally high instantaneous current during start?
(note that is the narrow focus of my question - I am not interested in talking about the setpoint).
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
2-pole motor ~ 50hp fed from ungrounded 480 vac system.
Motor tripped on instantaneous overcurrent a few months ago.
As part of investigation - Meggered/bridged motor (sat). Did a start while monitoring current on O-scope (sat). Checked molded case breaker instantaneous trip (sat - within expected bounds based on nameplate LRC and up to factor of 2 increase in 1st peak due to dc component). Breaker was replaced at that time.
Motor has not shown any unusual vibration or other characteristics.
Now this weekend - Motor tripped again on start (instantaneous). Motor meggers and bridges sat again. Voltage is normal.
They called me up at home and want to know: "Is there anything about the motor that can make it susceptible to causing a trip?"
My response is: No. The highest instantaneous peak varies in a random manner based on phase at closing (as we all know). None of the previous tests have shown anything abnormal. I have never heard of a 460vac motor fault that would lead to an instantaneous trip, and then motor subsequently operates fine. I think you need to check your setpoints and make sure they are high enough.
Their response is: the setpoints have been fully checked and are well above that theoretical worst case. We are on the verge of changing out the motor instead of re-revaluating the setpoint. We want to know what is it about the motor that can cause variation in starting current beyond what is predicted by analysis using 2* factor and nameplate data.
Can you help with this question? Any credible faults on the motor that cause an assumed (by others) abnormally high instantaneous current during start?
(note that is the narrow focus of my question - I am not interested in talking about the setpoint).
=====================================