We have a pumping system to circulate amine in closed loop consisting of columns, filters etc and back to the storage tank.
Now this pump is a axially split casing type 4 stage pump making the fluid reach 60 kg/cm2 at pump discharge. Tank is atmospheric pressurized tank.and level in tank never goes below 6 meters. Pump suction line is in same horizontal plane always I.e. whatever the head is available in tank, same reached to pump suction. There is one suction strainer installed in the line and suction line is around 25 meter long.
I feel cavitaion like sound coming from the pump. I saw pump test curve which shows that NPSH required at this point is 5 Meters. Operating temperature of fluid is 40 deg C.
I have few doubts,
* I assume the cavitation may be taking place in first stage only. Is it possible for cavitaion not occuring in 2nd and third stage as pressure is high in these stages and liquid may not be vapourising?
* pump suction line is 16" in size and there are 4 elbows in total in suction line.Strainer is clean.
* other than vaporisation of liquid, is there any other scenario that may be happening and making that cavitation type noise.
* NPSH required is 5 meter absolute pressure and available is 5 meter in tank + 10 meter corresponding to atmospheric pressure - max 5 meter for frictional losses I.e. not less than 10 Meters. From this calculation I don't think that pump should cavitate. But in real it sounds like cavifation.
Please give your valuable inputs.
Thanks a lot.
We have a pumping system to circulate amine in closed loop consisting of columns, filters etc and back to the storage tank.
Now this pump is a axially split casing type 4 stage pump making the fluid reach 60 kg/cm2 at pump discharge. Tank is atmospheric pressurized tank.and level in tank never goes below 6 meters. Pump suction line is in same horizontal plane always I.e. whatever the head is available in tank, same reached to pump suction. There is one suction strainer installed in the line and suction line is around 25 meter long.
I feel cavitaion like sound coming from the pump. I saw pump test curve which shows that NPSH required at this point is 5 Meters. Operating temperature of fluid is 40 deg C.
I have few doubts,
* I assume the cavitation may be taking place in first stage only. Is it possible for cavitaion not occuring in 2nd and third stage as pressure is high in these stages and liquid may not be vapourising?
* pump suction line is 16" in size and there are 4 elbows in total in suction line.Strainer is clean.
* other than vaporisation of liquid, is there any other scenario that may be happening and making that cavitation type noise.
* NPSH required is 5 meter absolute pressure and available is 5 meter in tank + 10 meter corresponding to atmospheric pressure - max 5 meter for frictional losses I.e. not less than 10 Meters. From this calculation I don't think that pump should cavitate. But in real it sounds like cavifation.
Please give your valuable inputs.