CDEGS Potential Plot values (Spot levels x 1.E+3)

Status
Not open for further replies.

jhm1090

Electrical
Apr 13, 2023
1
Hello,

I'm trying to understand the reason why the maximum and the threshold values in the plot snip attached show as 1.E+3 instead of the actual values. Is it because of some kind of an error in MALZ design, or we see that when the values are > 10,000 V?

Thank you.
 
 https://files.engineering.com/getfile.aspx?folder=e6a44382-9c70-475d-9069-b48568deb082&file=Capture.PNG
Replies continue below

Recommended for you

Maybe I'm missing something, but I interpret the plot as having a maximum value of 17,950 V (17.95 x 1E3 (1000). Minimum threshold (which can be set in CDEGS) is 822 V.
 