jwilson3
Electrical
- Dec 20, 2001
- 45
Several manufacturers recommend that a three phase delta-delta transformer, with the 240V secondary center tapped to serve lighting or other 120V loads, should have the 120 volt load limited to only 5% of the kva rating of the transformer because of the resulting loading caused by circulating currents.
I understand the circulating currents caused by impedance unbalance. I also recognize the limits of serving 240V single phase loads from a 240V delta winding, but that limit is as high as 50% of rating if no three phase load is being served.
I've tried to analize this arrangement to establish the amount of circulating current, but have not been successful.
If anyone can direct me to a good resource that covers this topic, it would be appreciated.