Sorry for the tongue twister.
This is more of a field observation and I'm curious whether anyone else has encountered a similar problem.
Focus- systems built from the late '80's into the '90's and equipped with Central/Gem with Belleville (brass cup) seats.
Back story-
I'm sure most on here remember the nightmare that was Central's call-it-anything-but-a-recall recall of O-ring style heads. During that same period the non-recall heads with Belleville seats went through a number of redesigns as well, presumably in a effort to find an effective, durable design. It seems that some of those designs were better than others.
My story-
We're finding sprinkler heads of this age with seats that have slipped ever so slightly off and allowing a tiny bit of water to seep out. The specific conditions are always consistent:
1. The heads are always Central, Gem, or other heads made under that corporate umbrella in the the years mentioned before.
2. High water pressure in the system, either from a pump or just crazy high city pressure, in excess of 120 psi.
3. The cup that the glass bulb rides in is much shallower than more recent heads, looking more like a section of a ball than current ones that are shaped more like a shot glass.
4. The slippage is very gradual. Early on it's likely that the seepage (from uprights) will evaporate before enough can collect on the bottom of the fitting to actually drip off. If one can get close enough, streaks of rust or paint discoloration will be visible. Pendent heads will develop a green or black streak on the frame or the deflector.
5. When it does start actively dripping on the floor it becomes obvious why once a close look is possible.
In the past five years I've probably ran into this a half a dozen times. Some systems had over 60% of the heads seeping to varying degrees.
Has anyone else had to deal with this type of thing?
Alex Traw
Rainbow Fire Sprinklers
Albany, Oregon
This is more of a field observation and I'm curious whether anyone else has encountered a similar problem.
Focus- systems built from the late '80's into the '90's and equipped with Central/Gem with Belleville (brass cup) seats.
Back story-
I'm sure most on here remember the nightmare that was Central's call-it-anything-but-a-recall recall of O-ring style heads. During that same period the non-recall heads with Belleville seats went through a number of redesigns as well, presumably in a effort to find an effective, durable design. It seems that some of those designs were better than others.
My story-
We're finding sprinkler heads of this age with seats that have slipped ever so slightly off and allowing a tiny bit of water to seep out. The specific conditions are always consistent:
1. The heads are always Central, Gem, or other heads made under that corporate umbrella in the the years mentioned before.
2. High water pressure in the system, either from a pump or just crazy high city pressure, in excess of 120 psi.
3. The cup that the glass bulb rides in is much shallower than more recent heads, looking more like a section of a ball than current ones that are shaped more like a shot glass.
4. The slippage is very gradual. Early on it's likely that the seepage (from uprights) will evaporate before enough can collect on the bottom of the fitting to actually drip off. If one can get close enough, streaks of rust or paint discoloration will be visible. Pendent heads will develop a green or black streak on the frame or the deflector.
5. When it does start actively dripping on the floor it becomes obvious why once a close look is possible.
In the past five years I've probably ran into this a half a dozen times. Some systems had over 60% of the heads seeping to varying degrees.
Has anyone else had to deal with this type of thing?
Alex Traw
Rainbow Fire Sprinklers
Albany, Oregon