FFP1
Mechanical
- Jan 22, 2007
- 211
I can only find the following references regarding the requirement that a centrifugal horizontal split case fire pump must have a positive suction supply.
6.1.2* Application. Centrifugal pumps shall not be used where a static suction lift is required.
A.6.1.2 The centrifugal pump is particularly suited to boost the pressure from a public or private supply or to pump from a storage tank where there is a positive static head.
I have a location with six 2,000 gpm @ 100 psi centrifugal horizontal split case fire pumps. I recently performed the annual flow test activities. This is a new customer for us, but the pumps have been in place for 15+ years. They area all arranged to take suction from an open top reservoir (approximately 100 ft. x 100 ft.) which is 15 ft. deep. The reservoir water level is 1 ft. above the top of the fire pump, so the STATIC suction pressure is 0.5 psi when the reservoir is completely full. Technically (based on the text listed above), this is acceptable based on NFPA. I do not think this arrangement should be considered acceptable. Centrifugal horizontal split case fire pumps are intended for applications which have positive suction pressures. What will happen after the deluge systems have operated for 30-60 minutes and the reservoir is 5-10 ft. below full?
Has anyone else seen a similar arrangement? Is this an acceptable arrangement based on NFPA?? Are there any NFPA requirements which I am missing which indicate this arrangement is unacceptable??
Thanks in advance!
6.1.2* Application. Centrifugal pumps shall not be used where a static suction lift is required.
A.6.1.2 The centrifugal pump is particularly suited to boost the pressure from a public or private supply or to pump from a storage tank where there is a positive static head.
I have a location with six 2,000 gpm @ 100 psi centrifugal horizontal split case fire pumps. I recently performed the annual flow test activities. This is a new customer for us, but the pumps have been in place for 15+ years. They area all arranged to take suction from an open top reservoir (approximately 100 ft. x 100 ft.) which is 15 ft. deep. The reservoir water level is 1 ft. above the top of the fire pump, so the STATIC suction pressure is 0.5 psi when the reservoir is completely full. Technically (based on the text listed above), this is acceptable based on NFPA. I do not think this arrangement should be considered acceptable. Centrifugal horizontal split case fire pumps are intended for applications which have positive suction pressures. What will happen after the deluge systems have operated for 30-60 minutes and the reservoir is 5-10 ft. below full?
Has anyone else seen a similar arrangement? Is this an acceptable arrangement based on NFPA?? Are there any NFPA requirements which I am missing which indicate this arrangement is unacceptable??
Thanks in advance!