timbones
Mechanical
- Jul 8, 2003
- 68
First, some background...
I have a closed loop cooling water system in which the pressure losses were over estimated. The circulation pump is a 100 hp centrifugal with a 14.5" impellor. The design flow rate is 1300 gpm with a TDH of 180 feet. When the pumps were started up the TDH was about 90 feet and the flow meter was reading totally off scale and off the pump curve (in excess of 2000 gpm). The plant manager was concerned that the high flow rates would lead to erosion problems in the exchangers and piping so some orifice plates were installed to boost the TDH and knock the flow rates down. The system now runs near the design conditions.
I would like to trim the pump impellor down to 13" from 14.5" to improve the efficiency of the system. If I leave in the current orifice plates or put in slightly larger orifices, I should be fine in terms of getting sufficient flow. If I completely remove the plates, I estimate the TDH will drop to 60 feet and the flow increase to 1600 gpm. This point is somewhat off the pump curve but I am not sure what that means. Will I run into problems with stable operation of the pump at such a low discharge pressure? Are there implications to the life of my pump? Will I draw more current through my motor than if I left the plates in (making it almost pointless to remove them)? Suggestions?
I have a closed loop cooling water system in which the pressure losses were over estimated. The circulation pump is a 100 hp centrifugal with a 14.5" impellor. The design flow rate is 1300 gpm with a TDH of 180 feet. When the pumps were started up the TDH was about 90 feet and the flow meter was reading totally off scale and off the pump curve (in excess of 2000 gpm). The plant manager was concerned that the high flow rates would lead to erosion problems in the exchangers and piping so some orifice plates were installed to boost the TDH and knock the flow rates down. The system now runs near the design conditions.
I would like to trim the pump impellor down to 13" from 14.5" to improve the efficiency of the system. If I leave in the current orifice plates or put in slightly larger orifices, I should be fine in terms of getting sufficient flow. If I completely remove the plates, I estimate the TDH will drop to 60 feet and the flow increase to 1600 gpm. This point is somewhat off the pump curve but I am not sure what that means. Will I run into problems with stable operation of the pump at such a low discharge pressure? Are there implications to the life of my pump? Will I draw more current through my motor than if I left the plates in (making it almost pointless to remove them)? Suggestions?