Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SDETERS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cf for Cable Tray waterfalling

Status
Not open for further replies.

ads0221

Civil/Environmental
Dec 12, 2016
43
I have a quick question. In general wind loads on cable trays we use Cf = 2.0 for all wind loadings going laterally against.

When we get a transition portion say from a pipe bridge to pipe rack at a lower elevation when the cable tray is vertical and we want to model the wind loads normal to the tray for the "waterfall" portion F = qz*G*Cf*A is Cf of 2.0 still used? In the "Wind Loads for Petrochemical and Industrial Facilities" publication they give a design example however only use Cf = 1.0.

Any thoughts are welcomed.

Thanks,
 
Replies continue below

Recommended for you



This is true for lateral load calc. for the rack .. But for longitudinal load calculation on pipe bridge, the cable trays jumps to EL 36.0 from 30.0 .

And the trays are sloped say 30 degr. ( pls look Figure 6.1.3 Pipe Bridge Example )

The vertical prjection area of cable trays = 0.9 x 20 ft x 6 ft = 108.0 ft2 ( assuming the solidity ratio 0.9)

Cf may be estimated from

- Table 5.3 ( with assumption a/b=0.25 , c/b= 3.2) Cf=1.2
- ASCE 7 Figure 30.8-2 ( Pitched free roof )

Probably Cf=1.0 is selected considering the cable trays are perforated and for simplicity..

 
Thank you for the detailed response. Our cable trays will be going at a 90 deg angle and thus could ASCE 7 Figure 29.4-1 "Solid Freestanding Sign" be used as well?
 


I would prefer ASCE 7-16 ( FIGURE 29.3-1 Design Wind Loads (All Heights): Force Coefficients, Cf, for Other Structures— Solid
Freestanding Signs )

Cf varies betw 1.30-1.95 . I would reduce the figure as per solidity ratio .
 