Realistic hypothetical: Lets say you are designing an office with DX split systems and the load calc comes to:
35,700 sensible btu/h
3,500 latent btu/h
39,200 Total.
This could probably be covered nicely by a nominal 3.5 ton system pretty nicely. Now lets say the cooling cfm required is 1595 based on a 20 degree TD. Would you size your unit based on the capacities, or select a unit that can be the CFM.
I struggle with this a lot with offices because of the high sensible heat ratios where I will have a 0.95 + sensible heat ratio. Any opinions?