Hi,
I have two questions :
Q# 1) Is it true that charging current is only avaiable in single conductor cables and is zero in case of three conductor cables because the magnetic field gets cancelled ?
Q# 2) For the first time I came across a situation I noticed that motors contribute to single line to ground fault as well. When I analyzed the short circuit report I found that +ve seq current and -Ve seq. Current are there but zero seq. current is zero.
I was under the impression that only Motors only contribute to three phase current. Is it true that single phase current contribution because of the unbalanced voltage due to ground fault.
I would appreciate a comment.
Thanks