richburton
Specifier/Regulator
- Dec 11, 2009
- 19
I am a commercial plan reviewer trying to maintain my mathematical skills which helps me do a better job while reviewing proposed structural projects submitted by engineers.
The attached problem illustrates a new overhead door cut into an existing masonry wall.
The criteria includes a deflection limit of L/600, 36 ksi steel, and a ground snow load of 30 psf. Rather than calculate the live and dead load for the roof, I simply assigned a value of 40 psf. The total load is then 20,819 lbs of masonry and roof being supported by the new steel lintel.
Please confirm or correct the following:
1) Max. moment = 31.23 kip-ft
2) Bending stress = 23,641 psi
3) required section modulus to resist failure due to bending = 15.85 in^3
4) required moment of inertia to resist deflection = 116.3^4
Thank you for volunteering your time.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner