Hi Noway2 -- I'm not saying your measurements are off, but I would be very suspicious of them.
![[rednose] [rednose] [rednose]](/data/assets/smilies/rednose.gif)
See calcs for the 6000 GPM / 12.6 kW case below.
I work with very big machines and plants too, university campus type stuff. I've never measured a difference across a pump that was larger than the error of the sensor/input combination except when the pump was running backward due to mis-wiring. Yours may indeed be an exception, but I can't explain how it would happen.
Now, I asked y'all above to shout out any silliness in my math. I'll be embarrassed as heck if there's a factor of 10 or 100 that I'm missing in here. Don't let me down. I can still do some math, but I'm no electricpete.
12.6 kW * 3413 BTU/KWH ÷ (6000 GPM x 8.33 LBM/G x 60 MIN/HR) = 0.014°F ΔT across pump in the chilled water stream.
Reversing the equation, the amount of power that would have to be lost in the water to create a 0.3°F ΔT across the pump would be:
0.3°F x 6000 GPM x 8.33 LBM/G x 60 MIN/HR ÷ 3413 BTU/HR/KW = 264 KW
It takes beaucoup heat to raise the temperature of 6000 GPM. 12 KW won't do the job.
OFF TOPIC TEMPERATURE SENSING RANT FOLLOWS! Read at your peril.
Note: the following pertains to HVAC type instrumentation. If you're in an industrial environment, your sensors might already be very accurate and your SCADA may be very precise. In our world, neither are really suitable for measuring tenths of a °F.
I've had to graduate into the extreme-accuracy RTDs and transmitters due to an absolutely silly building code in a country that I shall not name. The code requires that the chilled water temperature
at the controller be ±0.05°C (±0.09°F). Oh my goodness. Even with a 1/10 DIN RTD (±0.03°C or ±0.054°F
AT 0°C), a sniper-accurate transmitter, and 4-wire lead compensation, the ambient temperature variation error in both the sensor and the electronics knock the actual sensed accuracy up into unacceptable ranges for the building authority there. That is, unless you are his favorite local supplier. They actually take the whole rig -- sensor, transmitter, controller -- to the national standards lab to determine acceptability if you claim to be compliant and you do not have cigars each evening with the inspector. I have actually beaten that standard by quite a bit on the bench by careful calibration. But put it on a plane, send it across the an ocean, install it in the field and you'll find that it's out of the accuracy span by as much as 50 percent. That's verified by my own testing, too, not just the national lab there.
Describe your RTD / transmitter / SCADA type and wiring, Noway2, there may be a multiplication of error even if the RTD itself is accurate. Add the error sources above to the fact that the building automation system may be trying to resolve 0.1°F out of a 0-100°F 4-20 mA current loop with an A/D converter that might be only 8-bit. No way (no disrespect intended to your handle, Noway2
![[roll2] [roll2] [roll2]](/data/assets/smilies/roll2.gif)
).
It's tough to confirm that the spec I'm ranting about has been met unless the RTD is 4-wire, the transmitter is excellent ($$$), the controller has been calibrated to the nubs, and the ambient temperature of both the transmitter and the controller are kept fairly close to the temperature at which they were calibrated.
End of rant. Thank you for your patience. I hope I haven't offended any HVAC automation system suppliers.
Best to you,
Goober Dave