Chilled water buffer vessel size

Status
Not open for further replies.

Cooky

Mechanical
Jan 14, 2003
114
Does anyone have an equation that will calculate the required volume for a chilled water buffer vessel?

I use a 'rule of thumb' of 3 litres of fluid per kW of nett cooling, but I am after an equation that takes other variables into account. Such as number of chiller starts per hour, flow rates, desired temperature fluctuation.......

Thanks for your help.
 
Replies continue below

Recommended for you

3 litres/kW cooling seems a bit low to me. My experience is more like 7 litres/kW.

Brian
 
Brian,

With Carrier chillers, you can use as little as 2.5 - 3.0 litres / kW for an air conditioning application. If you need tight temperature control (such as a process application), then 7.0 - 8.0 litres / kW is my reccomendation.

Best regards,

Cooky
 