Chilled water system economy cycle thro' cooling towers

Status
Not open for further replies.

remp

Mechanical
Sep 15, 2003
224
I have an application that has a large chilled water demand even in the middle of winter. It goes down to -5 deg C outside here regularly in winter and the outdoor temp is below 5 deg C for 15% of the year...


Can I use the cooling towers to provide cooling directly to the chilled waetr system via a heat exchanger...

Does 5degC outside mean I can get the cooling tower down to 5 degC?

Has anybody try this before, any literature on it anywhere on the web on how you would pie it and control it.


Thanks
 
Replies continue below

Recommended for you

Sure, there are a number of ways of doing it. Sump heaters in the tower to prevent freezing when there is no flow. Insulated and heat traced condenser piping. Then pipe to a plate heat exchanger.

I was just reviewing an existing installation that used a Trane chiller with economizer mode for free cooling. The chiller uses convection of the refrigerant to cool the chilled water.

There should be details of a water-side economizer in the ASHRAE Handbooks.

Tower Tech towers have some descriptions of this application as well.
 