DRWeig
Electrical
- Apr 8, 2002
- 3,004
Friends,
I've walked up on a chiller with the following settings on its breaker:
Instantaneous pickup 6400A
Short-time pickup 4800A
Short time 0.3s
Earth pickup 640A
Earth time 0.3s
Here's the chiller data. Note it's a Y-Delta starter.
Motor LRA= 2616 A
Primary RLA = 473 A
Min circuit ampacity 601 A
Max overload protection + 1000 A
I am suggesting the following breaker settings:
Instantaneous pickup 3500A
Short-time pickup 1000A
Short time 0.5s
Earth pickup 1000A
Earth time 0.5s
Would you confirm that I'm close to the correct settings? Any other suggestions?
Best to you,
Goober Dave