Mendit
Mechanical
- Sep 12, 2003
- 95
We recently rebuilt a chiller motor (600hp 3600rpm)It had a die cast rotor. The motor failed from broken rotor bars.
We removed all the old die cast alum, manufactured new rotor bars and shorting rings from alum, all sizes were dulicated within 1-2%. The rotor bars are welded to the shorting rings. The motor has been installed. it starts and runs up to speed in approx 3-4 seconds, inrush current is normal, no load current is (normal 250 amps), however when the IGVs are opened to allow the freon to flow the motor current increases to 320 amps and does not compress the freon. The chiller company (Carrier) say the chiller clearances are fine and all is working well, there is plenty of freon in the system. Puzzled ?
We removed all the old die cast alum, manufactured new rotor bars and shorting rings from alum, all sizes were dulicated within 1-2%. The rotor bars are welded to the shorting rings. The motor has been installed. it starts and runs up to speed in approx 3-4 seconds, inrush current is normal, no load current is (normal 250 amps), however when the IGVs are opened to allow the freon to flow the motor current increases to 320 amps and does not compress the freon. The chiller company (Carrier) say the chiller clearances are fine and all is working well, there is plenty of freon in the system. Puzzled ?