Chiller Primary & Secondary Pump Flow Rate

Status
Not open for further replies.

Timothi

Mechanical
Feb 4, 2011
17
Experts,
I request your valuable comments on the case below,

Two numbers of 80 TR (W,S) chillers are installed for a commercial building of 100 TR cooling demand. Chillers are designed considering 20% diversity factor. There is a constant flow primary pump set with water flow rate 200 GPM (2.5gpm/TR). Should we maintain VFD secondary pump set water for at 250 gpm or 200 gpm is sufficient? Kindly advise




Sharing knowledge is the best way to learn
 
Replies continue below

Recommended for you

The whole point of having a VFD on your secondary system is that the flow will vary. So you will not have a constant 200 GPM or 250 GPM. You most likely have 2-way valves on the air handler coils, so the secondary flow can get much lower than 200 GPM during light load conditions.
 
A diagram/schematic of the system would be helpful.
 