remp
Mechanical
- Sep 15, 2003
- 224
I have 2 chillers working nicely on duty/stand by set up. Each chiller is rated for 2400kw and approx 100L/s each and CHW F&R temp of 6/12 Deg C. It is a primary /secondary set up so the flow thro the chillers is constant and the variable speed secondary pumps vary the flow to the building. Only one chiller ever runs at a time. The flow thro the chillers are fix thro an automatic balance valve (set and cannot be changed).
The building AHU's are a 2-port set up.
Here'e the problems, well so says an energy consultant we engaged recently;
When the chiller is running at low load we never get the chilled water return temperature back at 12deg C. The consultant reckons becasue it is a 2 port system the desing flow and return should always be 6/12 deg C.
It is usually about 8 or 9 deg C with only a 3 deg split and not the 6 deg split you would expect.
The consultant reckons there must be a by pass at an end of line loop in the building open that is causing this problem and letting CHW at 6 deg C mix with the return water form the AHu;s and reducing the overall CHW retrun temp.
My question is, if the building is at say 1/2 load and every AHU is only dropping the air by 50% of its design capacity does this automatically mean we have 50% the design water flow rate thro it....isnt the consultant automatically assuming the heating coil which is a heat exchanger has a perfect corelation between load and flow rate (direct proportion)....in other words half the flow and you half the capacity, 1/4 the flow and you 1/4 the capacity...is this true??? Isnt every heat exchanger different....Is there really a problem with the system set up?
The building AHU's are a 2-port set up.
Here'e the problems, well so says an energy consultant we engaged recently;
When the chiller is running at low load we never get the chilled water return temperature back at 12deg C. The consultant reckons becasue it is a 2 port system the desing flow and return should always be 6/12 deg C.
It is usually about 8 or 9 deg C with only a 3 deg split and not the 6 deg split you would expect.
The consultant reckons there must be a by pass at an end of line loop in the building open that is causing this problem and letting CHW at 6 deg C mix with the return water form the AHu;s and reducing the overall CHW retrun temp.
My question is, if the building is at say 1/2 load and every AHU is only dropping the air by 50% of its design capacity does this automatically mean we have 50% the design water flow rate thro it....isnt the consultant automatically assuming the heating coil which is a heat exchanger has a perfect corelation between load and flow rate (direct proportion)....in other words half the flow and you half the capacity, 1/4 the flow and you 1/4 the capacity...is this true??? Isnt every heat exchanger different....Is there really a problem with the system set up?