Chiller Tonnage

Status
Not open for further replies.

jthjr

Electrical
Mar 26, 2004
8
Can someone tell me the tonnage for the following three chillers from their model numbers?

York YTG1A1B2-CGH8
York YCWJ55HE0-46PA
York YCWZ33AB0-46PB

Is this information avaiabe in either Preston's Guide or Technical Reference Guide by Carson Dunlop?

Or is there a different refence guide for commerical HVAC equipment that has this type of info?

Thanks.
 
Replies continue below

Recommended for you

I have done both in the past.

I guess I was trying to see if someone would give the tonnage answers and then mention they got them out of a book. And then tell me you can get the book at...

Thanks for your reply.
 
The second and third chiller has a nominal tonnage of 55 and 33 tons, respectively. (use the 5th and 6th digits)

I got this from the technical guide book, you can get that from the manufacturer. (or website)

knowledge is power
 
@cdxx139 - These numbers refer to the size of each of the recip compressors. ie. two #5's. This is in the posted manual which I also found but doesn't tell much more. It gives the compressor part numbers, but not the nom. tons of each. The OP would need to take the comp part numbers to the manufacturer, in which case may as well just send the chiller number.
 
Again, websearching:
LCWT
LEAVING CONDENSER WATER TEMPERATURE (°F)
°F
85.0 90.0 95.0 100.0 105.0
TONS KW MBH EER TONS KW MBH EER TONS KW MBH EER TONS KW MBH EER TONS KW MBH EER

MODEL YCWJ55HE0
IPLV = 17.5
40.0 136.2 118.0 2037.0 13.9 132.5 122.8 2009.0 12.9 128.7 127.5 1979.0 12.1 124.9 132.1 1949.0 11.3 121.1 136.5 1918.0 10.6
42.0 141.5 119.0 2104.0 14.3 137.6 124.1 2075.0 13.3 133.8 129.0 2045.0 12.4 129.8 133.7 2013.0 11.7 125.9 138.3 1982.0 10.9
44.0 146.9 119.9 2172.0 14.7 142.9 125.3 2142.0 13.7 138.9 130.3 2112.0 12.8 135.0 135.3 2081.0 12.0 130.8 140.0 2048.0 11.2
45.0 149.7 120.4 2206.0 14.9 145.6 125.8 2176.0 13.9 141.5 131.0 2145.0 13.0 137.5 136.0 2114.0 12.1 133.4 140.8 2081.0 11.4
46.0 152.4 120.8 2241.0 15.1 148.3 126.4 2211.0 14.1 144.2 131.7 2180.0 13.1 140.1 136.8 2147.0 12.3 135.9 141.7 2114.0 11.5
48.0 158.1 121.6 2312.0 15.6 153.9 127.4 2281.0 14.5 149.6 132.9 2249.0 13.5 145.4 138.2 2216.0 12.6 141.1 143.3 2182.0 11.8
50.0 163.9 122.2 2384.0 16.1 159.6 128.3 2353.0 14.9 155.2 134.1 2320.0 13.9 150.9 139.6 2286.0 13.0 146.4 145.0 2252.0 12.1

MODEL YCWZ33AB0
IPLV = 17.3
40.0 55.3 45.7 820 14.5 53.8 47.8 809 13.5 52.3 49.8 797 12.6 50.7 51.8 785 11.7 49.1 53.8 773 11.0
42.0 57.5 46.0 846 15.0 55.9 48.2 835 13.9 54.4 50.3 824 13.0 52.8 52.4 812 12.1 51.2 54.4 799 11.3
44.0 59.7 46.3 874 15.5 58.1 48.5 863 14.4 56.5 50.7 851 13.4 54.9 52.9 839 12.5 53.2 55.0 826 11.6
45.0 60.8 46.4 888 15.7 59.2 48.7 876 14.6 57.6 50.9 865 13.6 56.0 53.1 852 12.6 54.3 55.3 840 11.8
46.0 61.9 46.5 902 16.0 60.3 48.8 890 14.8 58.7 51.1 878 13.8 57.0 53.4 866 12.8 55.3 55.6 853 12.0
48.0 64.2 46.8 930 16.5 62.6 49.1 918 15.3 60.9 51.5 907 14.2 59.2 53.8 894 13.2 57.5 56.1 881 12.3
50.0 66.6 47.0 959 17.0 64.9 49.4 947 15.8 63.2 51.8 935 14.6 61.5 54.3 923 13.6 59.7 56.6 910 12.7

TTFN

FAQ731-376
 
Search the RLA/LRA numbers from the nameplate in the available models similar to yours, those coming close to the listed RLA/LRA are your hits.
 