gonefishn
Mining
- Apr 14, 2009
- 5
We have a large chiller loop (~40k gal)that distributes chilled (-40F) methanol water (60%/40%) to a large number of heat exchangers and condensers. We recently had a 316L ss condenser welded tube failure at the welded seams. Attack appears to have occured from the methanol water side. The first failure occured after 10+ years of service. The second failure occured in about 4 months. Testing revealed a level of 300-400 ppm chlorides. We do not have a good history of chloride levels in the methanol water but theorize it is likely primarily contamination from the process side (the higher pressure side) during the first failure. The high chlorides then possibly caused chloride attack resulting in the second failure. The questions are:
1. Should this level of chlorides (300-400 ppm) at this temperature (-40F)cause this expedited corrosion rate?
2. Does anyone have experience removing chlorides from low temperature methanol water? Return temp is about -30F. System is must run so any filtering process must be done at -30F and can't significantly impact the chiller system performance, i.e, supply temp.
1. Should this level of chlorides (300-400 ppm) at this temperature (-40F)cause this expedited corrosion rate?
2. Does anyone have experience removing chlorides from low temperature methanol water? Return temp is about -30F. System is must run so any filtering process must be done at -30F and can't significantly impact the chiller system performance, i.e, supply temp.