rrmiv
Structural
- Mar 13, 2003
- 46
In reading thread507-104685, it got me wondering about the necessity of diaphragm chords being continuous. Suppose you have a steel deck diaphragm attached to a CMU wall (200' long) via a “continuous” angle bolted to the wall. The wall is designed as a shear wall when the shear force is parallel with it. If the wall has control joints (say every 20') and all horizontal reinforcement (including bond beam) stops at these joints, then the long wall acts as ten individual shear walls. The angle doesn’t even have to be truly continuous.
However when the shear force is in the other direction, the wall itself can act as a chord. It seems to me the same ten individual walls can serve as the chord (again resisting in-plane shear forces), although not continuous. The forces into these walls are not equal - the force increases as you approach the point of maximum moment in the diaphragm.
Is my thinking correct?
However when the shear force is in the other direction, the wall itself can act as a chord. It seems to me the same ten individual walls can serve as the chord (again resisting in-plane shear forces), although not continuous. The forces into these walls are not equal - the force increases as you approach the point of maximum moment in the diaphragm.
Is my thinking correct?