CIP Concrete Anchor Breakout Supplemental Reinforcement

Status
Not open for further replies.

cs0997

Civil/Environmental
May 4, 2023
1
I am designing cast in place anchors and the shear concrete breakout is exceeding the allowable, so I am designing supplemental reinforcement for the anchor group in order to negate the concrete breakout. Can anyone give some guidance on the design of this supplemental reinforcement?
 
Replies continue below

Recommended for you

My suggestion would be ,

- Pls look ACI 318 -19 , CHAPTER 17—ANCHORING TO CONCRETE

- Look also ACI 355.3R-11 ( there are worked examples )

- You may consider horizontal hairpins, anchor angle with reinf, shear lug ..

- You may prefer to provide more details to get more specific responds..

Excerpt from ANCHORAGE DESIGN FOR PETROCHEMICAL FACILITIES ( by ASCE Committee)

anchor_shear_reinf_rufxbb.jpg








I cannot give you the formula for success, but I can give you the formula for failure..It is: Try to please everybody.
 