CIP concrete shear wall with concrete beam framing

Status
Not open for further replies.

vvaccare

Structural
Jan 3, 2014
18
US
Good morning everyone,

Currently working on a concrete structure. Mostly CIP beams and columns, with shear walls as my lateral system. I am currently calling for 6000 psi concrete for the shear walls. Due to building and architectural constraints, I am limited in the width of my concrete beams. My question for the community is this. If/when you have a concrete beam framing perpendicular to the concrete shear walls, how do you typically deal with the required development length for your concrete beam hooked bars into the shear walls? These beams are going to help transfer my lateral loads to the shear wall system.

In my situation, I currently would need #7 bars for my beam design. I thought of trying to use a smaller size bar to ensure my development length into the shear wall is adequate, but due to the limited width of my concrete beam, I can only physically fit a certain number of bars to ensure proper concrete placement. This means that I currently would need a minimum hook length of 9.5" to get proper development. I've thought about multiple top and bottom layers of longitudinal reinforcing, but was hoping to avoid that if possible.

All this being said, say you had a 10" shear wall. For the sake of conversation, lets assume 1.5" of cover. That would leave us with 8.5" available for your ldh for any reinforcing being hooked into the shear wall. What methods can be done to ensure that the beam reinforcing placed into the shear wall achieve the necessary development length?

I know the easy answer would be to say to increase the shear wall thickness or beam dimensions, but I was hoping to start a conversation about other possible alternatives. Or even see if anyone has any other ways around this predicament. Any thoughts, comments, or input are greatly appreciated!
 
Replies continue below

Recommended for you

Can you clarify why you suggest that shear force is coming into a shear wall which is perpendicular to the beam?

If it is shear parallel to the wall then it would usually be dragged in via the slab, not by individual beams.

If it is shear perpendicular to the wall why would the wall participate other than deformation compatibility.

Can you apply As(reqd/ As(provided) but still meet minimum hook embedment depth?

 

1) The first thing to realize is that this is a bar anchorage problem rather than a bar development problem. Even if you could get Ldh on your bars, that may not be enough.

2) I second JAE's suggestion that, if at all possible, it would be preferable to deliver your shear through a slab to wall connection rather than at this beam connection.

3) If there's a wall parallel to the beam behind the beam, coupling some beam bars to some wall bars might be an option. If there is not such wall, this connection may not be such a hot idea.

 