Has anyone the installation specs for an old Westinghouse MC3800F circuit breaker? I'd like to know the recommended torque for the 1/2-13 bolt that mounts the 2 hole lug to the load side terminals.
The reason- I've a MCC that has exhibited the same symptom of spontaneous circuit breaker trips through 2 changes of the circuit breaker. (MC3800F thermal magnetic; MC800 rating plug; shunt trip). The machine (400Hp, 460V, 3Ø driven compressor) is soft started and will run lightly loaded for 1/2 to 10 hours before the circuit breaker will simply open up. The RVMS has been replaced as part of a general upgrade and both its internal monitoring and our external data-logging show no changes in the load(~150KW) before the trips.
When I removed the lugs from the load terminals, it took excessive effort to break the bolts loose. I remember another installation where an excessively tightened ØB bolt caused a malfunction of the push to trip button but that is not the case here.
Can the torque of the external connections significantly affect the thermal characteristics of a CB such as this?
The reason- I've a MCC that has exhibited the same symptom of spontaneous circuit breaker trips through 2 changes of the circuit breaker. (MC3800F thermal magnetic; MC800 rating plug; shunt trip). The machine (400Hp, 460V, 3Ø driven compressor) is soft started and will run lightly loaded for 1/2 to 10 hours before the circuit breaker will simply open up. The RVMS has been replaced as part of a general upgrade and both its internal monitoring and our external data-logging show no changes in the load(~150KW) before the trips.
When I removed the lugs from the load terminals, it took excessive effort to break the bolts loose. I remember another installation where an excessively tightened ØB bolt caused a malfunction of the push to trip button but that is not the case here.
Can the torque of the external connections significantly affect the thermal characteristics of a CB such as this?