I believe this was inapropriately posted in Electric Motors and Motors Control Engineering so I am reposting it here.
FORGIVE ME FOR DOUBLE POSITNG!
I have a customer asking for assistance with selecting the correct main circuit breaker for a 10HP 460V triplex vacuum system. Depending on the demand, only one unit could be in operation or all three could be operating at the same time. Motor FLA is 14 each (w/0 1.15 SF).
Cutler Hammer Motor Circuit Selector says the following:
1. Instantaneous trip circuit breaker GMPC/HMCP: 30 AMPS and
2. Circuit breaker trip rating: 35 AMPS
A.) Can someone provide a briefly explain the difference between #'s 1 and 2? and
B.) Should the breaker be sized based on all three units in operation (10HP x 3 = 30HP)?
Just trying to help a guy out!
Thanks!