Circuit Breaker Sizing for 30 KW Motor 1

Status
Not open for further replies.

tahirinst

Electrical
Nov 21, 2008
6
I need to install circuit breaker on 3 Phase Motor ( 30 KW). This motor is installed at Screw air compressor ( direct coupled). Motor voltage 400VAC, 50 Hz

Please advise size of breaker which should be installed. Motor Name Plate data is attached.
 
 http://files.engineering.com/getfile.aspx?folder=9e970a64-70b2-4127-b915-648d87f65459&file=Motor_Name_plate_data.jpg
Replies continue below

Recommended for you

In North America that is a matter of code compliance.
We reach for the Electrical Code book.
For DOL starting of a squirrel cage induction motor the code maximum is 250% of rated current with exceptions.
Consult your local code.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Hi tahirinst,

Are you sizing the CB that feeds the Air Compressor's Panel Board or the CB that will directly feed the motor?

Maybe a single line diagram will help us understand your requeriments

Regards.

JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"
 

CB will directly feed the three phase motor.....
 
Tah: If you are not using a contactor+relay scheme, you should use a "Motor Circuit Breaker" that has Thermal+Magnetic protection

You can just select it from a catalogue (i attach an example)

BEWARE: The rated Volts/frecuency/kA Icu must be in accordance with your installation

JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"
 
 http://files.engineering.com/getfile.aspx?folder=8ed731ee-c453-463f-aa3e-5100b614b4ec&file=GV3P.png