Circuit of the Future - fault current limiter

Status
Not open for further replies.

magoo2

Electrical
May 17, 2006
857
I read a news item last week where Southern California Edison announced their futuristic concept for distribution circuits. As news items go, this was sketchy on details.

What I've been able to gather is that this project had a lot of hands in it - Dept of Energy, EPRI, KEMA, etc.

One detail relates to the use of a fault current limiter. It is not clear where they would use them. Presumably it would be at the source end of the circuit.

Some details I found in the link


If anyone has more details to share on this topic, I'd be interested hearing about them.
 
Replies continue below

Recommended for you

Ah, are you absolutely sure that you're not thinking of the soon to be announced "fault anticipator'?

I'm on the waiting list for the first production run...

old field guy
 
They refer to the super conductor version. This device has a non-linear reactance; low at load current levels, high at fault levels. Nothing to reset, since it doesn't interrupt. It is used to allow better coordination of downstream equipment since fault currents are lower. I presume the solid state version is similar.
 