Circuit switcher fault interrupting

Status
Not open for further replies.

Mbrooke

Electrical
Nov 12, 2012
2,546
How is the primary interrupting capacity determined when clearing secondary faults? My understanding is the normal 25,000 amp value does not apply like it would for say a primary bushing flash over.


See page three:


 
Replies continue below

Recommended for you

Doesn't the page you referenced answer your question? If a secondary fault with an infinite primary system bus exceeds 4,000 A on the primary side, then it exceeds the interrupting rating. For instance, the primary fault current on a 15 MVA base rated 8% impedance, 115 kV transformer is 941 A. It is within the rating. The fault current for a 100 MVA, 8% impedance, 115 kV transformer is 6,276 A which exceeds the 4,000 A rating.
 
I guess I am wondering why the interrupting rating is low for a secondary fault yet so high for a primary fault?
 
The higher X/R ratio causes higher transient recovery voltage (TRV).
 
That would make sense then. Does S&C's equation apply to all faults (like L-G) as long as the true primary current does not exceed 4000 amps?
 
Note that the limit is not on actual fault current. It is on the current that would be in the primary for a 3Ø secondary fault with no system impedance (infinite source). A single phase fault will result in equal or lower primary fault current (depending on the transformer connection) so will not be the worst case.
 
Connection is delta wye grounded.

Would parallel operation of the secondary have any effect on interpreting?
 