Circuit Switcher Modeling

Status
Not open for further replies.

timm33333

Electrical
Apr 14, 2012
198
I am trying to figure out that how to model the motor operated circuit-switcher (with interrupter) for overcurrent coordination purposes? Software have the option to model circuit-breaker and disconnector, but no option to model circuit switcher. Thanks
 
Replies continue below

Recommended for you

Operated within its interrupting ratings, all you need is the interrupting time of the interrupter, the blades are a distraction. If the fault is beyond the interrupting rating and you try to interrupt it, well things can get interesting. We have several and have a blocking scheme to keep the CS from tripping until line tripping reduces the fault current below the interrupting rating. Fortunately I don't know how well that scheme actually works as we haven't had any faults that would require the blocking scheme since well before I started, if they've ever happened.

Modern circuit switchers, on the other hand, are essentially just live tank breakers and interrupt the same way breakers do.
 
You can just model it as a circuit breaker plus a disconnect switch unless you are trying to do some type of transient analysis on the device itself. Most software libraries include circuit switchers in their breaker library.
 