Hi All,
I am working on a rehab project where we are adding ties around a column that had broken ties and spalled cover concrete. For new columns we would lap by min 6" and hook the bars around the vertical bars. That is not feasible.
Lap for a #4 bar is 19", but the contractor has made ties that have a lap of about 12 inches. We are trying to utilize these ties if possible, but I am not seeing anything in ACI that talks about circular ties that just lap, but this is not new construction it is a retrofit to an existing column.
My question is, is there a way of estimating what is required in terms of tie tension based on the column profile and loading to see if the 12" lap would provide enough development?
Thanks in advance for your help!
I am working on a rehab project where we are adding ties around a column that had broken ties and spalled cover concrete. For new columns we would lap by min 6" and hook the bars around the vertical bars. That is not feasible.
Lap for a #4 bar is 19", but the contractor has made ties that have a lap of about 12 inches. We are trying to utilize these ties if possible, but I am not seeing anything in ACI that talks about circular ties that just lap, but this is not new construction it is a retrofit to an existing column.
My question is, is there a way of estimating what is required in terms of tie tension based on the column profile and loading to see if the 12" lap would provide enough development?
Thanks in advance for your help!