Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

circular slurry concrete diaphragm walls

Status
Not open for further replies.

jdbpe1

Structural
Aug 16, 2010
3
I have a project for combined sewer outflows to design a concrete drop shaft. The idea is to construct a concrete slurry diaphragm wall below grade subject to external water and soil pressures. The wall will be subject to ring compression. What section of ACI is used for strength design per owner requirements. Is it section 10 or 14 for walls to determine nominal compressive capacity? The shaft is 60 feet in diameter and about 60 feet deep.
 
Replies continue below

Recommended for you

I would use Chapter 10, but if the owner has requirements use those so long as they are not less than the code.

Remember, while the water load may be symmetrical the soil load will almost certainly not be resulting in bending, not just uniform compression in the ring. Also, I imagine the ring will be cast in segments, you will need to account for the lack of continuity across these segments (ring of ball bearing type of problem)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor