vtpower
Electrical
- Jan 8, 2005
- 44
One more question on a totally seperate issue. At one of our substations, we have 15KV cables coming off the low side of a 34.5 / 12.47 KV transformer. This feeds our low side bus which feeds the four feeders. The cables are Jacketed Concentric Neutral cables and there are 3 - 500MCM copper cables per phase. All three of the same phase are in their own pipe, so there are three pipes, each pipe has a seperate phase. During an IR check, we noticed one of the concentric neutrals where it ties into the ground grid was hot. We amp probed it and found 300Amps flowing on the concentric neutral??? We checked the other three phases and found the same thing. This neutral is tied into the ground grid and all three neutrals are tied together. The only though was induced voltage on the neutral is causing a current flow but it is a very short run and this doesn't seem to make sense. Again, any insight anyone might have would be very appreciated. We also checked amperage directly on the Xo bushing of the transformer and found next to nothing as expected because of the balanced system.
Thanks.
Thanks.