Class 1, Div 1 Distance Requirements

Status
Not open for further replies.

derrick1

Industrial
Oct 3, 2007
1
Is there a certain distance that a non-explosion proof device can be in a class 1, div 1 area? For example, we have a room that is class 1, div 1. If the non-exp device is 10 feet away from the 'source' (flammable liquid), is that ok? Or it can't be in this area at all? (There is a door between this device and the source.

Thanks
 
Replies continue below

Recommended for you

derrick1,
If in the "classified area" the component should meet the criteria for that classification.
 
You need to take a look through NFPA 497.

You'll find that in open areas, the Class 1, Division 1, area is limited to a distance 5' from the source. The Class 1, Division 2 area is limited to a distance of 10' from the source.

In any case you don't want to make the determination as to where the Class 1, Division 1 area ends and the Class 1, Division 2 area ends. In many applications this has already been defined, which is typically the case in offshore applications.

A good reference is the "Crouse-Hinds Code Digest 2005". You can download this from the web at:

Regards
Dan Marr