Class 1E power feed separation

Status
Not open for further replies.

Designer82

Electrical
Jan 21, 2011
3
If I have a component that must receive class 1E power, how far upstream does that circuit need to be class 1E?IE, all the way to the Unit Auxiliary Transformer?

thanks
 
Replies continue below

Recommended for you

Generally, you're considering that Class 1E circuit traces back to the buss that is supplied by your emergency diesels. In our plant, our Class 1E buss is 4160V. It is normally fed from offsite power, which is NOT Class 1E. But, in the event the offsite power feed is lost, the emergency diesel generator supplies the power to the Class 1E buss. All of the components associated with the EDG's are safety related, thus assuring that you can provide power to the Class 1E equipment. Your unit aux transformer is likely NOT safety related.

So, for example, our Class 1E buss is 4160V, which feeds some important pumps, etc. and several 480V load centers. Those load centers then feed multiple other components and some 480V/240V/120V transformers that feed to other components/circuit panels. All of this is considered Class 1E. We also have similar systems that are not considered Class 1 to feed circuits that do not have safety related equipment/components. The primary difference is that the non-Class 1E systems do not have the backup emergency power supplies. So, if we lose offsite power, the non-Class 1E circuit will not have power.
 
thank you jpankask. Great explanation. So, for example, if I have a Class 1E field instrument with Class 1E wiring/connections to a local instrument panel (also 1E) but then power wiring from that local panel to distribution panelboards which are non-Class 1E, that would pretty much make having a 1E field instrument and wiring to local panel pointless wouldn't it?

thanks
 
Yes it would be pointless, and much more expensive than it needs to be. At our plant, everything in the Class 1E system is Class 1E, i.e. you wouldn't have Class 1E system down the distribution panel, then non-Class after that, because the non-Class 1E equipment could compromise the integrity of the Class 1E system.
 