clean agent system

Status
Not open for further replies.

cdafd

Specifier/Regulator
Aug 18, 2005
2,918
anyone know if there is a maximumn time delay allowed, once that detection has said dump?????????????

nfpa 2001 does not appear to have a max delay
 
Replies continue below

Recommended for you

CDA, this is from FM Data Sheet 4-9, Clean Agents. It parallels NFPA 2001 in most cases. I believe this is what you are after: 2.1.3.7.1 Provide a pre-discharge alarm and time delay sufficient to allow personnel evacuation prior to discharge. Limit the time delay to 30 seconds maximum after the appropriate detection signal(s) for system actuation have been received.
 