stretched2thin
Electrical
- Jul 30, 2002
- 45
NEMA gives guidelines for clearances between live parts and ground and also live parts between phases for system BIL ratings and system voltages. (SG 6 - 1990 Table 32-1)
However, as far as I can tell, it does not give clearances between live parts of different system voltages. I'm mainly concerned about clearances for HV bus in a substation.
My first impression is that you would consider the lowest system voltage to be grounded and use the phase-to-ground clearance requirement for the highest system voltage. In other words the clearance between the LV and HV bushing should be the Phase-to-Ground clearance given for the HV Bushing Voltage and BIL.
I base this assumption on my history of transformer testing. In testing HV-to-LV clearances for transformers, the lower voltage terminals are grounded during Hipot and Impulse tests. These are the main two tests that test HV-to-LV clearances.
I know the easiest answer is to use the larger of the two distances. However, if it is safe, it would be advantageous for us to go with the smaller distance requirement.
However, as far as I can tell, it does not give clearances between live parts of different system voltages. I'm mainly concerned about clearances for HV bus in a substation.
My first impression is that you would consider the lowest system voltage to be grounded and use the phase-to-ground clearance requirement for the highest system voltage. In other words the clearance between the LV and HV bushing should be the Phase-to-Ground clearance given for the HV Bushing Voltage and BIL.
I base this assumption on my history of transformer testing. In testing HV-to-LV clearances for transformers, the lower voltage terminals are grounded during Hipot and Impulse tests. These are the main two tests that test HV-to-LV clearances.
I know the easiest answer is to use the larger of the two distances. However, if it is safe, it would be advantageous for us to go with the smaller distance requirement.