AstroHouse
Computer
- Nov 6, 2014
- 5
I have been at logger heads with the designers for the past two years, my system has expansion vessel, degasser and pressurisation unit, my highest point is 10 mtrs and my lowest ground level. I have 3 turbocor chillers but only use 1 as my load is approx 280kw with a total design load of 740Kw. I have N+1 on my secondary pumps which means I run 2 at a time. My problem is that they insist that I run at a pressure of 5.2 bar and for this my pumps are running at 90% (which seem to leave me no room to take up the remaining 480kw of load. I would have thought this pressure much too high if the frictional losses had been calculated correctly. also my suction pressure is 2.3 bar and my discharge is 5.2bar.
this has been driving me crazy for the past two years as I have sever starvation in certain parts of the system which was supposedly balanced, but the balance sheet shows most of the DRV's as being 100% open and 13% of design flow.
I believe this could be a long post and any help would be gratefully received
this has been driving me crazy for the past two years as I have sever starvation in certain parts of the system which was supposedly balanced, but the balance sheet shows most of the DRV's as being 100% open and 13% of design flow.
I believe this could be a long post and any help would be gratefully received