In general, when you remove all feedwater heaters from service, a turbine manufacturer will advise not to operate at greater than the nameplate rating of the turbine. A turbine manufacturer will advise that a reduction in output below the nameplate rating is required if you remove a heater from service, but higher pressure heater(s) remain in service. In addition, a turbine manufacturer will also advise that a reduction in output below the nameplate rating is required if you remove non-adjacent heaters from service. The amount of reduction must be determined according to a particular manufacturer's recommendations.
Please note that as each high pressure feedwater heater is removed from service in sequence, starting with the highest pressure heater, the final feedwater temperature will be reduced. As the final feedwater temperature decreases, it will become more difficult for the boiler to produce the full (design) steam temperature. Operating at less than design steam temperature will result in increased moisture in the turbine exhaust, and consequently, a higher rate of erosion of the LP last stage blades. There may be other detrimental effects of operation at reduced steam temperatures depending on the configuration of the turbine.
Also remember that removing any feedwater heater from service will result in lower turbine efficiency.
Best of luck!