CSA O86:19 recommends aspect ratios for CLT shear walls to be between 2 and 4 to promote rocking instead of sliding.
If I have a 4m storey height, the wall lengths must be between 1m and 2m long to meet the aspect ratio requirements.
Now say the panel sizes are all 2m wide (still 4m tall). Am i allowed to make a 6m long shear wall segment if all of the panel to panel joints are connected with energy dissipated connections? The hold downs would still only be at the corners of the segment, so 6m apart. In this case the aspect ratio of the entire wall segment would be less than 2 but i think this is the intent of clause 11.9.3.5.3 and 11.9.3.3.1.
If I have a 4m storey height, the wall lengths must be between 1m and 2m long to meet the aspect ratio requirements.
Now say the panel sizes are all 2m wide (still 4m tall). Am i allowed to make a 6m long shear wall segment if all of the panel to panel joints are connected with energy dissipated connections? The hold downs would still only be at the corners of the segment, so 6m apart. In this case the aspect ratio of the entire wall segment would be less than 2 but i think this is the intent of clause 11.9.3.5.3 and 11.9.3.3.1.