- 65
I have two questions. 1) How does Control mode Density/Area(CMDA) Sprinklers differ from Control mode Specific Application(CMSA) Sprinklers. NFPA 13 (2010 Edition) section 14.2 & 14.3 describes these two. The design criteria for CMSA sprinklers is well described in Table 14.3.1 of NFPA13 but the design criteria for CMDA sprinkler (K-factor selection and Minimum operating pressure)is not described. Can anyone help on this.
2) I am designing a Fire sprinkler system for Warehouse which contains Class IV commodities with a storage height of 15ft. & ceiling height of 33ft. It has got Double row back to back rack with wooden pallets.
Hazard Classification - ordinary hazard Group-2
Commodity Classification - Class IV commodities.
Design Density - 0.3 gpm/ft2 section 14.2.4.2
Modified Design density based on height of storage - 0.225 gpm/ft2 section 14.2.4.3
As no description of K-factor is given, I am considering K-8 as per section 12.6.2. Any suggestions would be great help.